Siemens V20 F5 Fault: Converter I2t Overload

Quick answer

F5 on a Siemens SINAMICS V20 is the converter I2t fault, an overload of the converter. Siemens lists these causes: converter overloaded, load cycle too demanding, or motor power (P0307) exceeds the converter power capability (r0206). Siemens says the load cycle must lie within specified limits and P0307 must match r0206. Siemens also notes that F5 cannot be cleared until the converter overload utilization (r0036) is lower than the converter I2t warning level (P0294).

Safety: Only a qualified electrician should work on the drive, the motor or their wiring. Siemens' fault table tells you what to check, but changing parameters, checking cables or looking inside the drive is work for a trained person. Follow the safety instructions in the full SINAMICS V20 Operating Instructions before any work.

Fix it step by step

  1. Note the code.
  2. Check that the load cycle lies within the specified limits.
  3. Check that motor power (P0307) matches converter power (r0206).
  4. Wait until converter overload utilization (r0036) is lower than the I2t warning level (P0294); only then can F5 be cleared.

Still showing F5?

  • Related alarm: A505 (converter I2t warning level exceeded; current will be reduced if P0610 = 1). Siemens' remedy is to check that the load cycle lies within specified limits.

हिंदी में

Siemens V20 में F5 का मतलब है ड्राइव ओवरलोड (I2t)। कारण: ज़्यादा लोड, भारी load cycle, या मोटर पावर (P0307) ड्राइव (r0206) से ज़्यादा।

  1. Load cycle सीमा में हो।
  2. P0307 और r0206 मेल खाएं।
  3. r0036 का मान P0294 से कम होने तक F5 क्लियर नहीं होगा, इंतज़ार करें।

Questions people ask

Is my drive too small?

Siemens lists motor power (P0307) exceeding the converter power capability (r0206) as a cause and says they must match.