Siemens V20 F1 Fault: Overcurrent

Quick answer

F1 on a Siemens SINAMICS V20 is an overcurrent fault. Siemens' manual lists three causes: the motor power (P0307) does not correspond to the converter power (r0206), a short circuit in the motor leads, or earth faults. Siemens says to check that P0307 matches r0206, that cable length limits are not exceeded, that the motor cable and motor have no short circuits or earth faults, that the motor parameters and stator resistance (P0350) are correct, and that the motor is not obstructed or overloaded. Siemens also suggests a longer ramp-up time (P1120) and a lower starting boost (P1312).

Safety: Only a qualified electrician should work on the drive, the motor or their wiring. Siemens' fault table tells you what to check, but changing parameters, checking cables or looking inside the drive is work for a trained person. Follow the safety instructions in the full SINAMICS V20 Operating Instructions before any work.

Common causes

  • Motor power (P0307) does not correspond to the converter power (r0206)
  • Motor lead short circuit
  • Earth faults

Fix it step by step

  1. Note the code. Read parameter r0949: 0 or 22 = hardware reported, 1 = software reported.
  2. Check that motor power (P0307) corresponds to converter power (r0206).
  3. Check that motor parameters match the motor in use and the stator resistance (P0350) is correct.
  4. Increase the ramp-up time (P1120) and reduce the starting boost level (P1312).
  5. Have an electrician check that cable length limits are not exceeded and that the motor cable and motor have no short circuits or earth faults.
  6. Check that the motor is not obstructed or overloaded.

Still showing F1?

  • A501 (current limit) is the matching alarm. Siemens' remedy for it is "See F1", and for very small motors (120 W) under FCC at light load it says to use V/f operation.

हिंदी में

Siemens V20 में F1 का मतलब है ओवरकरंट (करंट बहुत ज़्यादा)। कारण: मोटर पावर (P0307) ड्राइव पावर (r0206) से मेल नहीं खाती, मोटर केबल में शॉर्ट सर्किट, या अर्थ फ़ॉल्ट।

  1. r0949 देखें: 0 या 22 = हार्डवेयर ने बताया, 1 = सॉफ़्टवेयर ने बताया।
  2. P0307 और r0206 मिलाएं, मोटर पैरामीटर और P0350 सही हों।
  3. Ramp-up time (P1120) बढ़ाएं, starting boost (P1312) घटाएं।
  4. इलेक्ट्रीशियन से चेक कराएं कि केबल की लंबाई सीमा से ज़्यादा न हो और मोटर केबल व मोटर में शॉर्ट सर्किट या अर्थ फ़ॉल्ट न हो।
  5. मोटर अटकी या ओवरलोड न हो।