Siemens V20 F4 Fault: Converter Overtemperature

Quick answer

F4 on a Siemens SINAMICS V20 means the converter is overheating. Siemens lists these causes: converter overloaded, ventilation inadequate, pulse frequency too high, surrounding temperature too high, or fan inoperative. Siemens says to check whether the load or load cycle is too high, that the motor power (P0307) matches the converter power (r0206), that the pulse frequency is set to its default value, whether the surrounding temperature is too high, and that the fan turns when the converter is running.

Safety: Only a qualified electrician should work on the drive, the motor or their wiring. Siemens' fault table tells you what to check, but changing parameters, checking cables or looking inside the drive is work for a trained person. Follow the safety instructions in the full SINAMICS V20 Operating Instructions before any work.

Fix it step by step

  1. Note the code.
  2. Check whether the load or load cycle is too high.
  3. Check that motor power (P0307) matches converter power (r0206).
  4. Set the pulse frequency to its default value.
  5. Check whether the surrounding temperature is too high and the ventilation is enough.
  6. Have an electrician check that the fan turns when the converter is running.

Still showing F4?

  • Related alarm: A504 (converter overtemperature warning level exceeded, so pulse frequency and/or output frequency is reduced depending on P0290). r0037[0] shows heat sink temperature and r0037[1] chip junction temperature.

हिंदी में

Siemens V20 में F4 का मतलब है ड्राइव ज़्यादा गरम। कारण: ओवरलोड, हवा का कम आना-जाना, pulse frequency ज़्यादा, आसपास का तापमान ज़्यादा, या पंखा बंद।

  1. लोड बहुत ज़्यादा न हो, P0307 और r0206 मेल खाएं।
  2. Pulse frequency default पर रखें।
  3. आसपास का तापमान और हवा चेक करें।
  4. इलेक्ट्रीशियन से चेक कराएं कि चलते समय पंखा घूमता है।

Questions people ask

Can a fan that is not working cause F4?

Siemens lists "fan inoperative" and "ventilation inadequate" as causes, and says the fan must turn when the converter is running.

What is the difference between F4 and A504?

A504 is the warning: the temperature warning level was exceeded and the drive reduces pulse or output frequency. F4 is the fault trip.