Siemens V20 F2 Fault: Overvoltage

Quick answer

F2 on a Siemens SINAMICS V20 is an overvoltage fault. Siemens lists two causes: the main supply voltage is too high, or the motor is in regenerative mode. Regenerative mode can come from fast ramp downs or from the motor being driven by an active load. Siemens says to check that the supply voltage (P0210) is within the limits on the rating plate, that the ramp-down time (P1121) matches the inertia of the load, that the required braking power is within limits, and that the Vdc controller (P1240) is enabled and set properly. Higher inertia needs longer ramp times; otherwise apply a braking resistor.

Safety: Only a qualified electrician should work on the drive, the motor or their wiring. Siemens' fault table tells you what to check, but changing parameters, checking cables or looking inside the drive is work for a trained person. Follow the safety instructions in the full SINAMICS V20 Operating Instructions before any work.

Fix it step by step

  1. Note the code. Read r0949: 0 = hardware reported, 1 or 2 = software reported.
  2. Have an electrician check that the supply voltage (P0210) lies within the limits on the rating plate.
  3. Check that the ramp-down time (P1121) matches the inertia of the load. Higher inertia needs a longer ramp time.
  4. Check that the Vdc controller is enabled (P1240) and parameterized properly.
  5. Check that the required braking power is within the specified limits. If a longer ramp is not possible, Siemens says to apply a braking resistor.

Still showing F2?

  • Related alarms: A502 (overvoltage limit reached, can occur during ramp down if P1240 = 0), A910 (Vdc_max controller de-activated) and A911 (Vdc_max controller active).

हिंदी में

Siemens V20 में F2 का मतलब है ओवरवोल्टेज। कारण: सप्लाई वोल्टेज बहुत ज़्यादा, या मोटर regenerative mode में (तेज़ ramp down या लोड मोटर को घुमा रहा है)।

  1. r0949 देखें: 0 = हार्डवेयर, 1 या 2 = सॉफ़्टवेयर ने बताया।
  2. इलेक्ट्रीशियन से सप्लाई वोल्टेज (P0210) रेटिंग प्लेट की सीमा में चेक कराएं।
  3. Ramp-down time (P1121) लोड की इनर्शिया के हिसाब से हो; ज़्यादा इनर्शिया पर लंबा ramp time चाहिए।
  4. ज़रूरी ब्रेकिंग पावर तय सीमा में हो।
  5. Vdc controller (P1240) चालू और सही सेट हो।
  6. लंबा ramp time संभव न हो तो ब्रेकिंग रेज़िस्टर लगवाएं।

Questions people ask

Why does F2 come when the motor stops?

Siemens says regenerative mode can be caused by fast ramp downs. Higher inertia needs longer ramp-down times (P1121); otherwise apply a braking resistor.

What is the Vdc controller?

Siemens says to check that the Vdc controller is enabled (P1240) and parameterized properly. Alarm A911 shows when the Vdc_max controller is working to keep the DC-link voltage below the level in r1242.