Siemens V20 F11 Fault: Motor Overtemperature

Quick answer

F11 on a Siemens SINAMICS V20 is a motor overtemperature fault. Siemens lists two causes: the motor is overloaded, or, on small motors run at a frequency below 15 Hz, the fault may occur even though the motor temperature is within limits. Siemens says to check whether the load or load step is too high, that the motor nominal overtemperatures (P0626 to P0628) are correct, and to check the motor temperature warning level (P0604). For the small-motor case: if the motor current is not above the nominal current on the motor rating plate and the physical motor temperature is within limits, set P0335 = 1.

Safety: Only a qualified electrician should work on the drive, the motor or their wiring. Siemens' fault table tells you what to check, but changing parameters, checking cables or looking inside the drive is work for a trained person. Follow the safety instructions in the full SINAMICS V20 Operating Instructions before any work.

Fix it step by step

  1. Note the code.
  2. Check whether the load or load step is too high.
  3. Check that the motor nominal overtemperatures (P0626 to P0628) are correct, and check the motor temperature warning level (P0604).
  4. For small motors run below 15 Hz: check that motor current is not above the rated current on the motor rating plate and that the motor's physical temperature is within limits. If both are true, set P0335 = 1.

Still showing F11?

  • Related alarm: A511 (motor overtemperature I2t). For it Siemens says to check P0604, P0625 (motor surrounding temperature), the nameplate data (quick commissioning; motor identification with P1900 = 2), the motor weight (P0344), and P0626–P0628 if the motor is not a Siemens standard motor.

हिंदी में

Siemens V20 में F11 का मतलब है मोटर ज़्यादा गरम। कारण: मोटर ओवरलोड, या छोटी मोटर 15 Hz से कम पर चलने पर, मोटर का तापमान ठीक होने पर भी यह फ़ॉल्ट आ सकता है।

  1. लोड या लोड स्टेप ज़्यादा न हो।
  2. P0626 से P0628 और P0604 सही हों।
  3. छोटी मोटर 15 Hz से कम पर: करंट नेमप्लेट से ज़्यादा न हो और मोटर का तापमान ठीक हो, तो P0335 = 1 सेट करें।

Questions people ask

What is A511?

Motor overtemperature I2t alarm: motor overloaded, or load cycles or load steps too high. It clears by itself once the cause is fixed.